On Thu, 3 Jan 2008 09:55:38 -0800 (PST), you wrote: >I've used the 2 wire RTDs before...essentially measure the voltage across the device for the temperature, but I've been asked to look at 3 wire or full bridge RTD's. Now, they talked like they are one and the same but I think a full bridge is a 4 wire? 4 wire seems simple enough in that it has a constant current source to get better accuracy but what about 3 wire devices? A current source that dumps into a common ground? Just need some clarification on that. > With 4 wire, you apply current on one pair and measure voltage differentially on the other. Easiest way is to apply a constant-ish current, and take the ADC reference as the voltage across a precision series resistor in the excitation leg - this gives a direct reading of resistance independent ( within reason) of the excitation current, avoiding the need for expensive voltage references. 3-wire makes the reasonable assumption that the voltage drop on both excitation wires is the same. Assume the wires to one end are A,B and the other is C Apply current to A, with C grounded Measure voltage across B & C - this is the RTD voltage plus the voltage drop on the C wire Measure voltage between A and B - this is the voltage drop on the A wire. Subtract this value from the BC reading to get the 'real' RTD voltage value. -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist