I'll add a few things here... Current-mode signals are generally less susceptible to electronic noise (= than=20 voltage-mode signals), so great for sensors in industrial or other noisy=20 environments. When read by an A/D, the dynamic range (voltage) can be set simply with a= load=20 resistor. (Though I recently had a situation, where to get the voltage-r= ange=20 I needed, the load resistor would've surpassed the A/D max source impedan= ce=20 value). With a simple buffer op-amp with gain=3D1, this issue is solved. Also, although you lose a bit of range by eliminating the 0-4mA range fro= m the=20 transducer, it's easy to detect sensor/signal failure (at least in case o= f an=20 open circuit) or non-existence if the output drops to 0mA. Yes, there are digital signal outputs that do a lot of this better, but t= he=20 analog signals are still in wide use today, and generally lower-cost. Cheers, -Neil. On Friday 04 July 2003 06:57, Mike Harrison scribbled: > Typical 4-20ma transmitters (transducers) are 2-wire devices, powered b= y > the line, and regulate the current through them according to the value = they > want to transmit. > > A typical system setup is a 24v PSU, connected to a transmitter and an > indicator, all in series. > > You take your power from whatever voltage appears across your device, w= hich > should be kept as low as practical - ideally below about 10V. > People like Lin.Tech and Maxim have many 4-20ma examples in app notes, > which should give you a general idea. > > If you need more power than you can draw off the line, you will usually > need to isolate the 4-20 loop from your extra power supply. -- http://www.piclist.com#nomail Going offline? Don't AutoReply us! email listserv@mitvma.mit.edu with SET PICList DIGEST in the body